Post by Admin on Sun Sep 25, 2011 8:57 pm

Consumer Units > http://www.ebay.co.uk/sch/i.html?_nkw=rcd+consumer+unit+wylex&_dmd=2&_frs=1&_sop=15&_trksid=p3286.c0.m359

I need to replace the Mains Distribution Unit first Very Happy


Which are best Guys ... I want individual trip switches RCD`s etc with a separate circuit to the outside Very Happy

I already have a separate circuit to the Kitchen.


_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Sun Sep 25, 2011 10:37 pm

Hi Mio

I would count how many MCB syou require. Also Duel RCDs and add a couple on for spares. You will need to Know what you are usiing at themoment . You can position the MCBs and RCDs to suit your system |MIne is very similar to this one http://www.ebay.co.uk/itm/WYLEX-15-WAY-DUAL-RCD-INSULATED-CONSUMER-UNIT-C-W-MCBS-/110748949814?pt=UK_BOI_CircuitBreakers_RL&hash=item19c926dd36 . But set up differentlty. ie Main RCD(80A) has Houshold 7 MCBs+ 1 spare. 2nd RCD(63A) has 2 MCB Has outside lights + garage door on 16A MCB and Pond on 32A MCB. Hope this helps.

Best REgards Dave


Last edited by DaveB on Sun Sep 25, 2011 10:49 pm; edited 1 time in total
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Sun Sep 25, 2011 10:39 pm

P.S forgot to mention in the 7 MCBs for the houesold one of the MCB 16A is where the Solar panels are connected via the Inverer.

Regards Dave

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Sun Sep 25, 2011 11:03 pm

DaveB wrote:P.S forgot to mention in the 7 MCBs for the houesold one of the MCB 16A is where the Solar panels are connected via the Inverer.

Regards Dave

How do I work out the MCB`s Dave ?

Do you have pics of the unit feeding the outside pond etc ? assuming one or more cables is fitted from house mains to supply the pond. scratch

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 12:08 am

Mio If you have the old tyoe unit with fuses have a look what the fuses are and use similar MCB
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 12:17 am

DaveB wrote:Mio If you have the old typse unit with fuses have a look what the fuses are and use similar MCB

I think I found it cheaper Dave .... Is this the same model Sweetie ?

http://www.tlc-direct.co.uk/Products/WYNHRS15SSLHI.html

My old fuse box is rubbish Dave 30 amp is the highest unit on the board.

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 12:34 am

That looks the same however the configuration might be different. ie you might need different RCD and MCB depending upon what you need. Mine is this

Starting from the right

Main Breaker 125 A

RCD switch 80 A

Followed by MCBs lights 10A, Hob 32 A,Sockets 32A, Shower 32A,garage 16A,Central Hteaing 10A, Solar PV 16 A, Followed by second RCD then MCBs

Outside lights 16 A, Pond 20 A.

Installationj especially with heavy cables can be tricky and should be carried out by a qualified professional.

Hope this helps

Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 12:53 am

I have from left to right 5A 30A 30A 15A 30A 15A .... Translate that into MCB`S for me please Dave Very Happy


This is an ancient fuse board but the Kitchen supply has been separated and fitted with RCD`s when it was all rewired.

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 3:28 am

Mio

I think you will be ok with 6A, 32 A, 32 A, 16A,16A , 32A and !6A. together with 25 or 32 A for pond on other RCD depending upon what you want to run of this.Check with the supplier that it comes with these MCBs . Also you could go for the same main MCB as me 125A Best regards Dave

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 4:09 am

DaveB wrote:Mio

I think you will be ok with 6A, 32 A, 32 A, 16A,16A , 32A and !6A. together with 25 or 32 A for pond on other RCD depending upon what you want to run of this.Check with the supplier that it comes with these MCBs . Also you could go for the same main MCB as me 125A Best regards Dave

The Ebay model comes complete with 12 MCB`s Dave hence the price differential ... the other sells these separate Rolling Eyes

These are the specs >

WYLEX 15 WAY DUAL RCD SPLITLOAD BOARD

INSULATED CONSUMER UNIT

COMPLETE WITH 12 MCBS

WHEN PURCHASING PLEASE CHOOSE FROM:

6/10/16/20/32/40/50 AMPS

Fully 17th Edition complian
- Highly flexible in configuration permitting any combination of RCD protected ways
- Factory Fitted 100 amp Mains Switch
- Dual RCD : 2 x80 amp 30mA RCD
- Plastic Insulated
- Highly versatile, allowing the user to choose how they configure the split-load.
- Full Din rail accepts any modular din mounted devices such as bell transformers and timers.
- Ample cable knockouts.
easy installation compared to other boards out on the market
- Side cut outs profiled to accept mini trunking.
- Large segmented rear cable entries to allow trimming to the precise cable entry size.
- Circuit identification labels providing clear understanding of outgoing ways.
- Generous cable room with neutral and earth bars mounted on the top of the enclosure.

****BUY NOW AT A VERY LOW COST OF £114.84****

Do I list them in the order you have posted when purchasing please ? and would the supply to the pond then take a 10 KW Heater ?

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 6:58 am

Mio a 10kw heater will take 43 amps so will require a 50 A MCB and one of the 80 A RCDs. You will probably have to put the 10 Kw heater on a seperate supply than the other pond equipment. I would also go for a higher mains breaker than 100A with the 10kw heater. Especially if you have an electric shower and electric cooker. Your electrictian friend will be able to see exactly what you have got and will need to do the job. Good luck dave

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 7:26 am

DaveB wrote:Mio a 10kw heater will take 43 amps so will require a 50 A MCB and one of the 80 A RCDs. You will probably have to put the 10 Kw heater on a seperate supply than the other pond equipment. I would also go for a higher mains breaker than 100A with the 10kw heater. Especially if you have an electric shower and electric cooker. Your electrictian friend will be able to see exactly what you have got and will need to do the job. Good luck dave

I was going to go ahead and buy it Dave prior to having it installed so need advice on what to have it include upon purchase ...

Hope i`m not frying your engineering brain cells here Sweetie ... but in terms of watts/kw ? how big a heater could be safely run on this particular 100 amp consumer unit safely iyho ?


_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 4:38 pm

Mio

You should already have a main fuse fitted in your fuse box which will give you an idea of what you need at the moment. Without any very large heaters such as 10 Kw

It all depends upon what else you are using. ie If you are using a 10 kw heater & a 10 kw shower you could potentially use 2X 43 A which is 86A then add in electrical hob say 4 A, electric fire 13 A and every thing else and you could be over your 100 A. However if you were to drop your heater to say 6 Kw and your shower is only 8 or 9 Kw and no electric fire then you should be OK with the 100A main breaker.

How much more would it cst to replace the breaker with a 125A. just to be sure?

Best REgards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 7:02 pm

DaveB wrote:Mio

You should already have a main fuse fitted in your fuse box which will give you an idea of what you need at the moment. Without any very large heaters such as 10 Kw

It all depends upon what else you are using. ie If you are using a 10 kw heater & a 10 kw shower you could potentially use 2X 43 A which is 86A then add in electrical hob say 4 A, electric fire 13 A and every thing else and you could be over your 100 A. However if you were to drop your heater to say 6 Kw and your shower is only 8 or 9 Kw and no electric fire then you should be OK with the 100A main breaker.

How much more would it cst to replace the breaker with a 125A. just to be sure?

Best REgards Dave

I was going to plumb a 3KW heater into the WLP too Dave and the Cooker is electric also Rolling Eyes and I would like the option of buying a bigger heater later on ... not to mention needing a spare for the QT.

The Wylex 100 amp mains breaker is factory fitted ... do you mean have an electrician simply remove it from the board and fit a bigger one like these ? http://www.tlc-direct.co.uk/Main_Index/Consumer_Units_Index/index.html?source=adwords&kw=MCB&gclid=COeVjbi4uqsCFYIMfAodGRfCdg or buy a consumer unit with one already fitted...

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Mon Sep 26, 2011 10:22 pm

Mio

I strongly advise you to contact your electrical friend and show him exactly what you want to do. because there is also cable lenths to consider. He will be able to advise accordingly and buy seperately what you need from somewhere local . This will save any confusion and or buying anything which is not needed. I only gave advice as to gain knowledge. I would be quite happy to carry this workout myself, on my own house . If I could actually see the full installation. Now with your new found knowledge you will be able to discuss what is needed and not be ripped off.Sorry if qI am unable to help further.

Best Regards dDave

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Mon Sep 26, 2011 10:33 pm

Dave Thank You for your help Sweetie Very Happy

I now know significantly more than I did previously re what to ask for ... so will put all this to Tony when I next see him .


_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Wed Mar 07, 2012 3:13 am

Dave ... Very Happy

Will this unit suffice for now Sweetie ? http://www.ebay.co.uk/itm/WYLEX-15-WAY-DUAL-RCD-INSULATED-CONSUMER-UNIT-C-W-MCBS-/110748949814?pt=UK_BOI_CircuitBreakers_RL&hash=item19c926dd36#ht_1361wt_906


_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Wed Mar 07, 2012 3:48 am

Mio

In most peoples cases I would say yes but for folks such as us who have I than normal needs. I can only repeat what I said previously and suggest you get your electrician friend to advise you after seeing the installation you already have first hand. Sorry if I can,t be more specific

Good luck with it I am sure you will get there in the end

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Wed Mar 07, 2012 4:08 am

DaveB wrote:Mio

In most peoples cases I would say yes but for folks such as us who have I than normal needs. I can only repeat what I said previously and suggest you get your electrician friend to advise you after seeing the installation you already have first hand. Sorry if I can,t be more specific

Good luck with it I am sure you will get there in the end

Good Idea ...

The Plasterer will be here thursday Dave ... who is the `Electricians` cousin Very Happy I will ask him to get him to take a look at the proposed Wylex or ask him to fashion a more apt one himself Very Happy

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Wed Mar 07, 2012 5:29 am

Definately the way to go

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Tue Mar 13, 2012 5:18 am

Been up to my eyes in Plastering debris which will be finished tomorrow Very Happy
The Electrician will call in tomorrow evening to discuss what type `Consumer Unit` we will need Very Happy

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Tue Mar 13, 2012 5:41 am

Good luck & let us know what you go with

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Thu Mar 15, 2012 6:24 am

The Electrician called and says the Wylex Consumer Unit is more than adequate for all our electrical needs Dave .. so I have just bought it in readiness for installation ...

Plastering finished now too Very Happy

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by DaveB on Thu Mar 15, 2012 6:14 pm

Well done, hope it all goes ok Keep us posted

_________________
Best Regards Dave
avatar
DaveB

Posts : 589
Join date : 2011-06-06
Age : 62
Location : Tyne & Wear England

Back to top Go down

Re: Wiring Upgrade

Post by Admin on Thu Mar 15, 2012 6:37 pm

The Wylex is twice the size the old Consumer Unit was Dave so will need relocating .... Very Happy

Looks like a good piece of kit though ... I chose 6/10/16/20/32/40/50 AMPS which the Electrician advised Very Happy

The pond will run on the 50 Amps on a separate RCD ...

Don`t you just love progress Sweetie Very Happy

_________________
MIO/CHICHI
avatar
Admin
Admin

Posts : 1970
Join date : 2011-02-08

http://mio-chichi.forumotion.co.uk

Back to top Go down

Re: Wiring Upgrade

Post by Sponsored content


Sponsored content


Back to top Go down

Page 1 of 2 1, 2  Next

View previous topic View next topic Back to top


 
Permissions in this forum:
You cannot reply to topics in this forum